The neutral conductor of a balanced 4-wire, three-phase wye circuit, that\'s at
ID: 2085980 • Letter: T
Question
The neutral conductor of a balanced 4-wire, three-phase wye circuit, that's at least 50 percent loaded with nonlinear loads (electric-discharge lighting, electronic ballasts, dimmers, controls, computers, laboratory test equipment, medical test equipment, recording studio equipment, and so forth) isn't considered a current-carrying conductor for the purpose of applying bundle adjustment factors.True or falss The neutral conductor of a balanced 4-wire, three-phase wye circuit, that's at least 50 percent loaded with nonlinear loads (electric-discharge lighting, electronic ballasts, dimmers, controls, computers, laboratory test equipment, medical test equipment, recording studio equipment, and so forth) isn't considered a current-carrying conductor for the purpose of applying bundle adjustment factors.
True or falss
True or falss
Explanation / Answer
False
A neutral conductor of a balanced 4 wire 3 phase Wye circuit with 50% non linear load produces nuetral current for sure but not upto 100%. So these are considered as a current carrying conductor for the purpose of applying bundle adjustment factors.