Steam enters a counter flow heat exchanger dry saturated at 10 bar and leaves at

ID: 707479 • Letter: S

Question

Steam enters a counter flow heat exchanger dry saturated at 10 bar and leaves at 350°C. mass flow of steam is 800 kg/min. The gas enters the heat exchanger at 650 °C and mass flo rate is 1350 kg/min. If the tubes are 30 mm diameter and 3m long, determine the number o tubes required. Take for steam: tsa-180°C (@i 0 bar); Cps?2. 71 kJ/kg°C, h.-600 w/m2°C Take for gas: Cpe 1 kJkg C, he 250 W/m2 C 3. 4. What is the significance of Reynolds No. in determining the heat transfer coefficient in forced convection? 5. What is the significance of Nusselt No. in determining the heat transfer coefficient in forced convection? 6. Prove that Prandtl No and Reynolds No. is a dimensionless quantity. 7. Write a short note on occurrence of radiation heat transfer in a process equipment.

Explanation / Answer

Ans 3

Steam inlet temperature at 10 bar

Tsi = 180°C

Steam outlet temperature

Tso = 350°C

Mass flow rate of steam

ms = 800 kg/min x 1min/60s = 13.33 kg/s

Cps = 2.71 kJ/kg-C

Gas inlet temperature Tgi = 650°C

Gas outlet temperature = Tgo

Cpg = 1 kJ/kg-C

Mass flow of gas

mg = 1350/60 = 22.5 kg/s

Heat given by gas = heat absorbed by steam

mg x Cpg x (Tgi - Tgo) = ms x Cps x (Tso - Tsi)

22.5 x 1 x (650 - Tgo) = 13.33 x 2.71 x (350 - 180)

14625 - 22.5Tgo = 6141.131

Tgo = 377.06 °C

Heat duty Q = 6141.131 kW

LMTD for counter flow

= [(650-350) - (377.06 - 180)] / ln (300/197.06)

= 244.94 °C

Overall heat transfer coefficient

1/U = 1/hs + 1/hg

= 1/600 + 1/250

= 0.005666

U = 176.47 W/m2-C

Area of exchanger

A = Q/UxLMTD

= 6141.131 * 1000 / 176.47 * 244.94

= 142.07 m2

Number of tubes = A/(3.14*D*L)

= 142.07/(3.14*0.030*3)

= 502.7

N = 503